Hi again,

So this is my new silencer design. I've increased the size of the paths for the supply and increased the ducting to 150mm. I'm planning on using metal spigots caulked and screwed to the boxes to attach my insulated flexible ducting between the silencers and to the fan etc.

Attachment:
New ventilation design.png


Attachment:
New ventilation design inside.png


Attachment:
New ventilation design below.png


I plan on using a 4 way ceiling diffuser for supply and probably exhaust too (mainly cosmetic reasons, continuity, and the datasheet says it's fine).

Thanks


You do not have the required permissions to view the files attached to this post.


Report this post
Top
 Profile  
 
PostPosted: Wed Mar 07, 2018 5:10 pm 
Offline
Moderator
User avatar

Joined: Wed Feb 01, 2017 6:03 pm
Posts: 1038
Location: St. Albert, Alberta, Canada
It looks awesome now!!!!

Greg

_________________
It appears that you've made the mistake most people do. You started building without consulting this forum.


Report this post
Top
 Profile  
 
PostPosted: Sat Mar 17, 2018 10:34 am 
Offline
Senior Member

Joined: Sat May 20, 2017 7:47 am
Posts: 304
Location: Surfleet, UK
Thanks Greg!

I've ordered the materials to build my ventilation system so I'm happy.

Back to construction!

Dan


Report this post
Top
 Profile  
 
PostPosted: Sat Mar 31, 2018 1:39 am 
Offline

Joined: Fri Mar 30, 2018 1:56 am
Posts: 1
Are you using any kind of fan to draw stale air out of the room? That's the dilemma I'm running into.


Report this post
Top
 Profile  
 
PostPosted: Sun Apr 08, 2018 5:24 am 
Offline
Senior Member

Joined: Sat May 20, 2017 7:47 am
Posts: 304
Location: Surfleet, UK
davepettitt wrote:
Are you using any kind of fan to draw stale air out of the room? That's the dilemma I'm running into.


Yes, you use a fan that can provide 6 air changes per hour to provide for comfortable oxygen requirements. So mine needs around 200CFM or 340 m3/h. The fan I've installed is an inline mixed flow fan that has 2 settings with the lower setting only 26db and provides 410 m3/h at free flow so should be fine:
http://www.ductstore.co.uk/acatalog/Sil ... -Fans.html


Report this post
Top
 Profile  
 
PostPosted: Sun Apr 08, 2018 7:41 am 
Offline
Moderator
User avatar

Joined: Wed Feb 01, 2017 6:03 pm
Posts: 1038
Location: St. Albert, Alberta, Canada
Dan! More pictures please!!

Greg

_________________
It appears that you've made the mistake most people do. You started building without consulting this forum.


Report this post
Top
 Profile  
 
PostPosted: Wed Apr 11, 2018 4:53 am 
Offline
Senior Member

Joined: Sat May 20, 2017 7:47 am
Posts: 304
Location: Surfleet, UK
Gregwor wrote:
Dan! More pictures please!!

Greg


Yup, more pics on the build thread:
viewtopic.php?f=10&t=21269


Report this post
Top
 Profile  
 
PostPosted: Tue Jul 10, 2018 5:44 am 
Offline

Joined: Wed Mar 14, 2018 4:37 am
Posts: 63
Location: Paris
Waka wrote:
Hi again,

So this is my new silencer design. I've increased the size of the paths for the supply and increased the ducting to 150mm. I'm planning on using metal spigots caulked and screwed to the boxes to attach my insulated flexible ducting between the silencers and to the fan etc.

Attachment:
New ventilation design.png


Attachment:
New ventilation design inside.png


Attachment:
New ventilation design below.png


I plan on using a 4 way ceiling diffuser for supply and probably exhaust too (mainly cosmetic reasons, continuity, and the datasheet says it's fine).

Thanks


Dan, what cross section do your silencer boxes have? Will the duct between the two silencers be 150mm?


Report this post
Top
 Profile  
 
PostPosted: Sat Jul 14, 2018 1:46 am 
Offline
Senior Member

Joined: Sat May 20, 2017 7:47 am
Posts: 304
Location: Surfleet, UK
Quote:
Dan, what cross section do your silencer boxes have? Will the duct between the two silencers be 150mm?


So the duct cross section is 17671.5mm2 and yes The duct between the silencers is also 150mm diameter.

The cross section inside the silencers is 150mm x 250mm = 37500mm2

I'm currently having to redesign the inner leaf silencer as I have less space between inner and outer leaf then on my sketchup design. It's looking like I will have it between the inner leaf joists instead of on top of them.

I'm going to post a new design for them soon (TM)

Dan


Report this post
Top
 Profile  
 
PostPosted: Sat Jul 14, 2018 12:18 pm 
Offline

Joined: Mon Jan 05, 2015 11:47 am
Posts: 74
Location: Apollo Bay, Australia
Waka wrote:
davepettitt wrote:
Yes, you use a fan that can provide 6 air changes per hour to provide for comfortable oxygen requirements. So mine needs around 200CFM or 340 m3/h. The fan I've installed is an inline mixed flow fan that has 2 settings with the lower setting only 26db and provides 410 m3/h at free flow so should be fine:
http://www.ductstore.co.uk/acatalog/Sil ... -Fans.html

Fire up that fan and let us know if it’s really producing only 26 dB. In my limited experience with “silent” mixed flow inline fans, the quoted specifications are usually miles away from reality. Worth checking before you install.

I purchased the following fan which claims to produce only 33db on high and 26db on low. On both settings the fan is about 30db louder than quoted. https://www.fansonline.com.au/fanco-tt- ... 150mm.html


Report this post
Top
 Profile  
 
PostPosted: Sat Jul 14, 2018 1:54 pm 
Offline
Senior Member
User avatar

Joined: Thu Aug 21, 2008 10:17 am
Posts: 11973
Location: Santiago, Chile
Quote:
Fire up that fan and let us know if it’s really producing only 26 dB. In my limited experience with “silent” mixed flow inline fans, the quoted specifications are usually miles away from reality.
Yep. :thu: Agreed!

- Stuart -

_________________
I want this studio to amaze people. "That'll do" doesn't amaze people.


Report this post
Top
 Profile  
 
PostPosted: Sat Jul 14, 2018 5:56 pm 
Offline
Senior Member

Joined: Sat May 20, 2017 7:47 am
Posts: 304
Location: Surfleet, UK
chrispire wrote:
Fire up that fan and let us know if it’s really producing only 26 dB. In my limited experience with “silent” mixed flow inline fans, the quoted specifications are usually miles away from reality. Worth checking before you install.

I purchased the following fan which claims to produce only 33db on high and 26db on low. On both settings the fan is about 30db louder than quoted. https://www.fansonline.com.au/fanco-tt- ... 150mm.html


Ye I did take it with a grain of salt, and the measurement is from 3m, so 1m away is more like 38db. It's actually installed already, but outside of the sealed middle leaf in the ventilated third leaf void, so any noise has to go through the silencers or the leaves before entering the room.


Report this post
Top
 Profile  
 
PostPosted: Sun Jul 15, 2018 2:29 am 
Offline
Senior Member

Joined: Sat May 20, 2017 7:47 am
Posts: 304
Location: Surfleet, UK
Ok so I think I've got a workable design for my inner leaf silencers now. I definitely don't have enough room to place them on top of the inner ceiling joist, so I've had to make the box breach the leaf itself (I'm going to have to be extremely precise making sure this is sealed properly). I've created a boxed section on top of the silencer to take the air to the other side of the box as the gap isn't big enough for the flex duct to get through. This means the diffusers are central in the ceiling (which I like) and the boxes are quite compact.

I think I've covered most of my bases with the new design, but they're a lot more complex then the outer leaf boxes.

From above:

Attachment:
New design inner leaf silencer inlet.jpg


Inlet images:

Attachment:
New design inner leaf silencer inlet below.jpg


Attachment:
New design inner leaf silencer inlet removed side.jpg


Extract images: I need a filter to stop room dust etc getting into my extract silencer/fan so I've added a slight dropped ceiling section with an access hatch on the front to replace the panel filter.
This dropped section consists of additional bass trapping and is located against the rear wall.

Attachment:
New design inner leaf silencer extract below.jpg


Attachment:
New design inner leaf silencer extract removed side.jpg


All of the brown coloured insulation will be covered by fabric stapled between the joists and the seams covered by wooden strips.


You do not have the required permissions to view the files attached to this post.


Report this post
Top
 Profile  
 
PostPosted: Sun Jul 15, 2018 3:59 am 
Offline
Moderator
User avatar

Joined: Wed Feb 01, 2017 6:03 pm
Posts: 1038
Location: St. Albert, Alberta, Canada
Innovative design! The size of these things make fitting them anywhere so difficult. I'm re-designing mine right now and it's proving to be a nightmare, just like yours :-(

Have you checked the specs on that register grill? Make sure it's quiet enough!

Greg

_________________
It appears that you've made the mistake most people do. You started building without consulting this forum.


Report this post
Top
 Profile  
 
PostPosted: Sun Jul 15, 2018 4:15 am 
Offline
Senior Member

Joined: Sat May 20, 2017 7:47 am
Posts: 304
Location: Surfleet, UK
Gregwor wrote:
Innovative design! The size of these things make fitting them anywhere so difficult. I'm re-designing mine right now and it's proving to be a nightmare, just like yours :-(

Have you checked the specs on that register grill? Make sure it's quiet enough!

Greg

They are indeed a pain!

I phoned them before I bought it. It has 50% free area, and is 450mm x 450mm. This allows quite alot more than the flow in the silencers, so it looks good to me. Silencer cross section is 37500mm2 and flow through diffuser is 50625mm2.


Report this post
Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 88 posts ]  Go to page Previous  1, 2, 3, 4, 5, 6  Next

All times are UTC + 10 hours


Who is online

Users browsing this forum: No registered users and 20 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Group